  1. Ken, I think you still have two issues, 1. intermittent problem with the communication between the eyebrow board and main circuit board. ( reason I am saying this is because we were able to cause the refig to fail when changing the temperature setting on the eyebrow board with flame on and 11” gas pressure at test port) 2. Oil in propane line restricting flow to other appliances. ( remember we only saw the manometer respond to changes in demand after we cleaned the rubber hose. Manometer was attached to rear propane port monitoring demand. I would change tanks as someone else suggested. ) It might be time to do something drastic and remove and clean copper lines, new rubber hose, and a different tank since you are now having more problems with the furnace and water heater.
×
×